ISA Interchange

Welcome to the official blog of the International Society of Automation (ISA).

This blog covers numerous topics on industrial automation such as operations & management, continuous & batch processing, connectivity, manufacturing & machine control, and Industry 4.0.

The material and information contained on this website is for general information purposes only. ISA blog posts may be authored by ISA staff and guest authors from the automation community. Views and opinions expressed by a guest author are solely their own, and do not necessarily represent those of ISA. Posts made by guest authors have been subject to peer review.

All Posts

Ask the Automation Pros: How to Best Migrate from Obsolete to Modern Instrumentation and Control Systems?

The following discussion is part of an occasional series, "Ask the Automation Pros," authored by Greg McMillan, industry consultant, author of numerous process control books, and 2010 ISA Life Achievement Award recipient. Program administrators will collect submitted questions and solicits responses from automation professionals. Past Q&A videos are available on the ISA YouTube channel. View the playlist here. You can read all posts from this series here.

Looking for additional career guidance, or to offer support to those new to automation? Sign up for the ISA Mentor Program.


Erik Cornelsen’s Question:

What are the most critical points to consider related to instrumentation and control systems when migrating a project from obsolete to modern versions?

Héctor H. Torres’ Responses:

Avoid control issues; consider differences in PID algorithms. The proportional–integral–derivative (PID) controller algorithm could vary from the obsolete to the modern version. There are three common PID forms that a control system could offer: parallel form, standard, also known as ISA form, and series, also known as classical form. Be aware that obsolete and modern control systems versions could default or use a different PID form, if tuning parameters are not “translated,” control issues are to be expected. In some, the integral action is in repeats per minute, in others, in seconds per repeat. The Derivative term could be required in minutes versus seconds. James Beall does a great job summarizing the differences in PID forms and provides formulas to convert series to tandard PID tuning in his presentation, “Interesting and Useful Features of the DeltaV PID Controller."

Scaling of devices. The importance of verifying the scaling of your devices cannot be stressed enough. List them and confirm the scaling is correct before start up. It is painful realizing a specific scale had not been properly set when fine tuning product ratios and rates, especially if the change requires a shutdown to correct. Make sure your devices list includes speed ranges and amperages, plus any other information considered valuable.

Communication protocols barrier. In cases where migration is conducted in phases, keep in mind virtual points that get shared between the to-be-migrated controllers and evaluate peer-to-peer communications between them. Build a spreadsheet containing all important details of these peer-to-peer virtual connections and validate these are still needed. Be specific about all changes required to remove these references. If still needed, determine the best way to keep that info between controllers. When minimal, hardwiring them between both systems could be an option with the use of auxiliary termination panels.

Migration diagram showing obsolete and modern systems

When the amount of shared information is considerable, using a hub concentrating all cross-communications is a good option. One of the replaced obsolete controllers acts as the hub. This controller maintains communication with the still-in-operation obsolete controllers and brings information back and forth between both obsolete and modern systems via a serial interface.

Working on a virtual machine minimizes cutover time and allows for testing. When a migration is conducted in a phased approach, the next controllers to be replaced are deleted from the virtual machine database to identify and correct all resulting errors from missing references. The corrected and free of errors database is imported to the production system, spending minimum time to instill the required modifications at cutover, and at minimum downtime.

Peter Morgan's Responses:

Adding to Hector’s response, although some features of the existing control strategies and their implementation might be better retired in the new system, the importance of understanding the functionality of the existing system cannot be underestimated. This may involve adding to existing documentation (if it exists at all), which can add to project costs. Adding this step may be resisted, but it increases the probability of a successful execution of the project. Not to be neglected are the discrete controls interfacing to motor control centers (MCCs) for pumps, fans, etc., since overlooking the interface requirements can result in unexpected and hazardous behavior.

To take advantage of the control system modernization as an opportunity to improve plant performance and operability, records such as loss control reports and recorded observations relating to major upsets should be taken into consideration. There is significant benefit in engaging operators in identifying where improvements can be made.

Well-developed written procedures for “swing over” should be considered essential for the successful commissioning of complex systems. This may involve identifying which systems are to be swung over on line and what temporary provisions are required to be put in place to make this possible. 

Pat Dixon's Responses:

I have done a bunch of migrations, and one of the critical differentiators is schedule. If schedule is less of a concern, you want to invest in a quality job using technology that is proven but also will have a long shelf life. The design and software component is where a lot of additional effort is required to make a state of the art system. Understanding the way functionality can be best implemented for performance and maintainability in a control system can require a lot of training and reading documentation. I have witnessed many poorly implemented migrations caused by failure to understand the native functionality built into a system. These are cases where startups are a nightmare, and once you finally have operation nobody wants to touch anything because the configuration and programming are a mess. Putting the effort into optimizing the implementation has huge benefits that can persist for the life of the system.

If you have a tight schedule, you may need to descope the effort. There are migration tools that can quickly convert configurations, but there will be some fixing required afterward. This may result in sub-optimal yet functional software. There are ways to reuse field terminations with adapters to more modern processors. The result can be a system that closely resembles the prior system, but the new system may have the same limitations that you wanted to improve with a more modern system. Beyond the technical methods, agile project management can compact a schedule. In agile, your team ideally co-locates, has daily updates and plans, implementation is presented continually for review and test instead of testing everything when done, and the design effort is reduced because you and the customer are designing continually in real time. For example, I managed a project that rebuilt a system destroyed by fire in two months with a modern system that the customer has loved for the last three years.

Sometimes the existing software logic and configuration isn’t entirely helpful for a migration. A written sequence of operations/functional specification, updated piping and instrumentation diagrams (P&ID), and input/output (I/O) lists can go a long way toward ensuring that the new system hits the mark.

As others have said, simulations (which we now call digital twins) are enormously beneficial to ensuring that you can go from factory acceptance test to site commissioning efficiently.

Hunter Vegas' Responses:

The answers above offer a lot of good advice. I will expound on Pat Dixon’s comments and then add a number of other suggestions that have not been covered.

Pat Dixon mentioned “schedule” – I’ll extend that concept by discussing shutdown logistics. Like the experts above, I have personally managed hundreds of control system migrations ranging from < 100 points to over 10,000 points. At our kick off meeting I always ask these questions:

  • How much time do we have to cut the system over (system shutdown to start up)?
  • Must any part of the plant keep working during some (or all) of the shutdown period?
  • Can commissioning/loop checks start early – i.e., can we start checking as soon as we get the first series of points cut over and energized?

Once I know the time frame, I can start looking at the existing system and begin formulating a plan for the job. Invariably the schedule will drive the design as well as the cost. A tight schedule can cost significantly more for a variety of reasons. For instance:

  • Reusing cabinets saves money but requires additional time to rewire.
  • Migration adapters/solutions offered to easily migrate from system A to system B are costly, but they can save time. (They also can have serious limitations, which is another discussion.)
  • If the I/O counts are high and the cutover time is very short, you may have to intercept wiring at the field junction boxes or even at the devices themselves and pre-wire back to new cabinets in another location. This can save a lot of time, but it is very costly.
  • Less time usually involves more people and longer shifts, reducing efficiency.

Another piece of advice I will offer is to do your homework on I/O compatibility. I have seen many a conversion project fail spectacularly because the design team did not fully understand how the existing I/O functioned. One must study the existing I/O in depth to fully understand all of its electrical characteristics to make sure the new I/O cards will work with the existing loops. Things to consider include:

  • Impedance of the analog input cards – older systems had much less impedance – 50 ohms or less was common. New systems are usually 250 ohms to allow Hart communications. If there are other devices in the loop, there may not be enough voltage to handle the new cards.
  • Grounding of analog cards – some analog cards are grounded while other analog cards are isolated. Grounded cards can create many problems:
    • The I/O card must be at the end of the loop or downstream devices will not work.
    • 4 wire I/O cards can have ground loop/noise problems if the field device is also grounded.
    • Grounded cards usually require a solidly grounded control system or noise can occur.
    • Grounded thermocouple cards may not work with grounded thermocouples.
  • Leakage current on digital I/O – new I/O tends to have very high input impedance and turns “on” at very low current. These cards can be incompatible with solid state field devices which leak enough current to turn on the input regardless of the field device state. This can be particularly problematic when wiring one DCS/PLC to another. Sometimes interposing relays are the only option but even some of the smaller relays have coils that can turn on with leakage current.
  • Current inrush on digital outputs – it is important to carefully examine the continuous and inrush current capabilities of the old and new digital cards. High density cards tend to have much lower current capability than the older digital output card designs with fewer points. If migration kits are being used, make sure they don’t further limit the current per channel. New cards seem to be much more sensitive to inrush currents and inductive kick back.

My parting advice is put your top people on the retrofit hardware design. Software can usually be adjusted relatively easily and quickly. Hardware design errors are expensive and often very difficult to resolve.

Greg McMillan's Responses with Links to Articles:

Take this opportunity to use advances in control valve precision and measurement accuracy and rangeability. For better control valves this means staying away from on-off valves that are enticing due to lower leakage and large capacity and seeking true throttling valves, such as globe valves with low friction packing, diaphragm actuators sized for at least 150% of max thrust or torque requirement and smart positioners. ISA-TR75.25.02 Annex A can provide the guidance needed as to the details and benefits of better throttling valves. For better measurements, this means using resistance temperature detector (RTD) sensors in spring-loaded stepped thermowells where possible, Coriolis and magnetic flowmeters where feasible, radar level where beneficial, and eliminating the many potential problems posed by impulse lines, purges, diaphragm seals, and capillaries.

Further reading: 

The many advances in PID technology should be tapped including the use of two degrees of freedom structure to improve setpoint response, directional move suppression via external-reset feedback and valve position control to eliminate the oscillations caused by split range point and an enhanced PID to provide much tighter, smoother control for wireless measurements and analyzers. ISA-TR5.9-2023 should be studied to get the most out of modern PID control capability.

Copy jobs should be avoided. Projects should take advantage of the increased capability offered by modern instrumentation and control systems by better feedforward and feedback control strategies including override control, procedure automation, and state-based control. Take advantage of dynamic simulations using the digital twin to spur innovation and provide the path to the development, testing, training, continuous improvement, and online metrics for success.  

Further reading: 

Greg McMillan
Greg McMillan
Greg McMillan has more than 50 years of experience in industrial process automation, with an emphasis on the synergy of dynamic modeling and process control. He retired as a Senior Fellow from Solutia and a senior principal software engineer from Emerson Process Systems and Solutions. He was also an adjunct professor in the Washington University Saint Louis Chemical Engineering department from 2001 to 2004. Greg is the author of numerous ISA books and columns on process control, and he has been the monthly Control Talk columnist for Control magazine since 2002. He is the leader of the monthly ISA “Ask the Automation Pros” Q&A posts that began as a series of Mentor Program Q&A posts in 2014. He started and guided the ISA Standards and Practices committee on ISA-TR5.9-2023, PID Algorithms and Performance Technical Report, and he wrote “Annex A - Valve Response and Control Loop Performance, Sources, Consequences, Fixes, and Specifications” in ISA-TR75.25.02-2000 (R2023), Control Valve Response Measurement from Step Inputs. Greg’s achievements include the ISA Kermit Fischer Environmental Award for pH control in 1991, appointment to ISA Fellow in 1991, the Control magazine Engineer of the Year Award for the Process Industry in 1994, induction into the Control magazine Process Automation Hall of Fame in 2001, selection as one of InTech magazine’s 50 Most Influential Innovators in 2003, several ISA Raymond D. Molloy awards for bestselling books of the year, the ISA Life Achievement Award in 2010, the ISA Mentoring Excellence award in 2020, and the ISA Standards Achievement Award in 2023. He has a BS in engineering physics from Kansas University and an MS in control theory from Missouri University of Science and Technology, both with emphasis on industrial processes.

Books:

Advances in Reactor Measurement and Control
Good Tuning: A Pocket Guide, Fourth Edition
New Directions in Bioprocess Modeling and Control: Maximizing Process Analytical Technology Benefits, Second Edition
Essentials of Modern Measurements and Final Elements in the Process Industry: A Guide to Design, Configuration, Installation, and Maintenance
101 Tips for a Successful Automation Career
Advanced pH Measurement and Control: Digital Twin Synergy and Advances in Technology, Fourth Edition
The Funnier Side of Retirement for Engineers and People of the Technical Persuasion
The Life and Times of an Automation Professional - An Illustrated Guide
Advanced Temperature Measurement and Control, Second Edition
Models Unleashed: Virtual Plant and Model Predictive Control Applications

Related Posts

Checking In With Mimo, ISA's Large Language Model Trained on ISA Content

Over the summer of 2024, the International Society of Automation (ISA) announced a large language model (...
Kara Phelps Nov 15, 2024 7:00:00 AM

Ask the Automation Pros: The Use of Artificial Intelligence in Process Control

The following discussion is part of an occasional series, "Ask the Automation Pros," authored by Greg McM...
Greg McMillan Nov 12, 2024 4:30:00 PM

Protecting Electrical Terminal Blocks From Tampering

Electrical terminal blocks are a common sight in the automation world. Usually mounted on DIN rail in ind...
Anna Goncharova Nov 8, 2024 10:30:00 AM